    Backup Protection of Transformer | Over Current and Earth Fault

    Backup Protection of Transformer | Over Current and Earth Fault

    Over Current and Earth Fault Protection of Transformer

    Backup protection of electrical transformer is simple Over Current and Earth Fault protection are applied against external short circuit and excessive over loads. These over current and earth Fault relays may be of Inverse Definite Minimum Time (IDMT) or Definite Time type relays (DMT). Generally IDMT relays are connected to the in-feed side of the transformer.
    The over current relays can not distinguish between external short circuit, over load and internal faults of the transformer. For any of the above fault, backup protection i.e. over current and earth fault protection connected to in-feed side of the transformer will operate.Backup protection is although generally installed at in feed side of the transformer, but it should trip both the primary and secondary circuit breakers of the transformer.Over Current and Earth Fault protection relays may be also provided in load side of the transformer too, but it should not inter trip the primary side circuit breaker like the case of backup protection at in-feed side. The operation is governed primarily by current and time settings and the characteristic curve of the relay. To permit use of over load capacity of the transformer and co-ordination with other similar relays at about 125 to 150% of full load current of the transformer but below the minimum short circuit current.Backup protection of transformer has four elements; three over current relays connected each in each phase and one earth fault relay connected to the common point of three over current relays as shown in the figure. The normal range of current settings available on IDMT over current relays are 50% to 200% and on earth fault relay 20 to 80%.Another range of setting on earth fault relay is also available and may be selected where the earth fault current is restricted due to insertion of impedance in the neutral grounding. In the case of transformer winding with neutral earthed, unrestricted earth fault protection is obtained by connecting an ordinary earth fault relay across a neutral current transformer.
    The unrestricted over current and earth fault relays should have proper time lag to co-ordinate with the protective relays of other circuit to avoid indiscriminate tripping.

    Transformer Protection and Transformer Fault

    There are different kinds of transformers such as two winding or three winding electrical power transformers, auto transformer, regulating transformers, earthing transformers, rectifier transformers etc. Different transformers demand different schemes of transformer protection depending upon their importance, winding connections, earthing methods and mode of operation etc.
    It is common practice to provide Buchholz relay protection to all 0.5 MVA and above transformers. While for all small size distribution transformers, only high voltage fuses are used as main protective device. For all larger rated and important distribution transformers, over current protection along with restricted earth fault protection is applied. Differential protection should be provided in the transformers rated above 5 MVA.
    Depending upon the normal service condition, nature of transformer faults, degree of sustained over load, scheme of tap changing, and many other factors, the suitable transformer protection schemes are chosen.
    Nature of Transformer Faults

    Although an electrical power transformer is a static device, but internal stresses arising from abnormal system conditions, must be taken into consideration.
    A transformer generally suffers from following types of transformer fault-

    1. Over current due to overloads and external short circuits,
    2. Terminal faults,
    3. Winding faults,
    4. Incipient faults.

    All the above mentioned transformer faults cause mechanical and thermal stresses inside the transformer winding and its connecting terminals. Thermal stresses lead to overheating which ultimately affect the insulation system of transformer. Deterioration of insulation leads to winding faults. Some time failure of transformer cooling system, leads to overheating of transformer. So the transformer protection schemes are very much required.
    The short circuit current of an electrical transformer is normally limited by its reactance and for low reactance, the value of short circuit current may be excessively high. The duration of external short circuits which a transformer can sustain without damage as given in BSS 171:1936.



    The general winding faults in transformer are either earth faults or inter-turns faults. Phase to phase winding faults in a transformer is rare. The phase faults in an electrical transformer may be occurred due to bushing flash over and faults in tap changer equipment. Whatever may be the faults, the transformer must be isolated instantly during fault otherwise major breakdown may occur in the electrical power system.
    Incipient faults are internal faults which constitute no immediate hazard. But it these faults are over looked and not taken care of, these may lead to major faults. The faults in this group are mainly inter-lamination short circuit due to insulation failure between core lamination, lowering the oil level due to oil leakage, blockage of oil flow paths. All these faults lead to overheating. So transformer protection scheme is required for incipient transformer faults also. The earth fault, very nearer to neutral point of transformer star winding may also be considered as an incipient fault.
    Influence of winding connections and earthing on earth fault current magnitude.
    There are mainly two conditions for earth fault current to flow during winding to earth faults,

    1. A current exists for the current to flow into and out of the winding.
    2. Ampere-turns balance is maintained between the windings.

    The value of winding earth fault current depends upon position of the fault on the winding, method of winding connection and method of earthing. The star point of the windings may be earthed either solidly or via a resistor. On delta side of the transformer the system is earthed through an earthing transformer. Grounding or earthing transformer provides low impedance path to the zero sequence current and high impedance to the positive and negative sequence currents.
    Star Winding with Neutral Resistance Earthed

    In this case the neutral point of the transformer is earthed via a resistor and the value of impedance of it, is much higher than that of winding impedance of the transformer. That means the value of transformer winding impedance is negligible compared to impedance of earthing resistor. The value of earth current is, therefore, proportional to the position of the fault in the winding. As the fault current in the primary winding of the transformer is proportional to the ratio of the short circuited secondary turns to the total turns on the primary winding, the primary fault current will be proportional to the square of the percentage of winding short circuited. The variation of fault current both in the primary and secondary winding is shown below.
    Star Winding with Neutral Solidly Earthed

    In this case the earth fault current magnitude is limited solely by the winding impedance and the fault is no longer proportional to the position of the fault. The reason for this non linearity is unbalanced flux linkage.

    لاإله إلا الله محمد رسول الله

  2. #2
    مشرف قسم المحولات الصورة الرمزية رباح فارس
    تاريخ التسجيل
    Oct 2007
    الدولة
    العراق
    المشاركات
    7,248

    رد: Backup Protection of Transformer | Over Current and Earth Fault

    شكرا لك مشاركة مفيدة
    قــال تعالـــى : (( وقــل أعملــــوا فسيـرى اللــه عملــكم ورســوله والمؤمنون )) صدق اللــه العظيـم

  3. #3
    Consultant Engineer الصورة الرمزية أسامة حسن البلخي
    تاريخ التسجيل
    Sep 2014
    الدولة
    مكة المكرمة
    المشاركات
    1,111

    رد: Backup Protection of Transformer | Over Current and Earth Fault

    جزاك ربي كل خير على سمو العبارة ، ورحم الله والديك
    لاإله إلا الله محمد رسول الله

  4. #4
    Senior Engineer الصورة الرمزية zackariya
    تاريخ التسجيل
    Apr 2010
    الدولة
    algeria
    المشاركات
    392

    رد: Backup Protection of Transformer | Over Current and Earth Fault

    بارك الله فيك مهندس على هذه المشاركة المميزة , ما رأيك في under-voltage protection في المحولات هل هي ضرورية؟

  5. #5
    Consultant Engineer الصورة الرمزية أسامة حسن البلخي
    تاريخ التسجيل
    Sep 2014
    الدولة
    مكة المكرمة
    المشاركات
    1,111

    رد: Backup Protection of Transformer | Over Current and Earth Fault

    إن هبوط الجهد يؤثر سلبياً على ملفات وأجزاء المحول أو انخفاض الجهد عن الجهد الأسمي ، ويجعل الخرج أقل قيمة من المطلوب فيتسبب باحتراق المحركات والضواغط و غيرها ، لذا لابد للمحولة من حمايات انخفاض جهد الدخل - هذا الملف فيه عموم توجيهات حماية المحولات
    الملفات المرفقة الملفات المرفقة
    لاإله إلا الله محمد رسول الله

  6. #6
    Senior Engineer الصورة الرمزية zackariya
    تاريخ التسجيل
    Apr 2010
    الدولة
    algeria
    المشاركات
    392

    رد: Backup Protection of Transformer | Over Current and Earth Fault

    شكرا لك سيدي الكريم, ولكن ألا تظن أن thermal overload تكفي عندهبوط الجهد علما أن التيار يكبر ؟

  7. #7
    Consultant Engineer الصورة الرمزية أسامة حسن البلخي
    تاريخ التسجيل
    Sep 2014
    الدولة
    مكة المكرمة
    المشاركات
    1,111

    رد: Backup Protection of Transformer | Over Current and Earth Fault

    لاتكفي ..لأن هذه الحماية تتحسس بالحرارة الناشئة عن ارتفاع الحمل .. وهذه الوظيفة يمكنك أن تحددها على منحنيات العمل في أجزاء تمثل هذه الخاصية ، فهي غير مشتركة مطلقاً مع وظائف حمايات تتعلق بأجزاء من منحنيات انخفاض التيار ... كل حماية لها عنصر تحسس يمثل نوع الحماية ، كالحماية المساقية المعنمدة على قيم المقاومات وأطوال الكابلات وبعدها عن العطل ، و الحمايات من ارتفاع التيار .. لها عنصر تحسس يمر به التيار سيفصل عند تعيير قيمة محددة للتيار ...
    لاإله إلا الله محمد رسول الله

معلومات الموضوع

الأعضاء الذين يشاهدون هذا الموضوع

الذين يشاهدون الموضوع الآن: 1 (0 من الأعضاء و 1 زائر)

المواضيع المتشابهه

  1. EARTH FAULT CURRENT
    بواسطة محمد الحايك في المنتدى قسم وقاية نظم القوى الكهربائية Power System Protection
    مشاركات: 2
    آخر مشاركة: 19-02-17, 11:47 AM
  2. RELAY SETTING CALCULATION OVER CURRENT AND EARTH FAULT
    بواسطة adel.ali في المنتدى قسم وقاية نظم القوى الكهربائية Power System Protection
    مشاركات: 2
    آخر مشاركة: 30-01-17, 10:23 PM
  3. EARTH FAULT CURRENT IN 6.6 KV SWITCHGEAR
    بواسطة amin elaro في المنتدى قسم صيانة المعدات الخاصة بمحطات التحويل Switchgear
    مشاركات: 0
    آخر مشاركة: 22-11-13, 02:59 AM
  4. difference between earth fault and over current???
    بواسطة Engineer Ali hassan في المنتدى قسم وقاية نظم القوى الكهربائية Power System Protection
    مشاركات: 22
    آخر مشاركة: 30-04-10, 11:28 PM
  5. VAMP140-Over Current and earth fault relay
    بواسطة م.هشام رمضان في المنتدى قسم كتالوجات أجهزة الوقاية
    مشاركات: 2
    آخر مشاركة: 15-06-06, 10:17 AM

المفضلات

المفضلات

ضوابط المشاركة

  • لا تستطيع إضافة مواضيع جديدة
  • لا تستطيع الرد على المواضيع
  • لا تستطيع إرفاق ملفات
  • لا تستطيع تعديل مشاركاتك
  •  

 

 

Flag Counter