    Simple question

    السلام عليكم ورحمة الله وبركاته
    Dear brothers
    I know that my question is simple but sometimes we might forget some principles
    In the attached file you will find a 66 33kV transfromer withDyn11 vector group
    the earth fault protection relay is connected to the CT installed on the transformer neutral point
    My simple inquiry is what will be the reaction of the earth fault relay in case of earth faults on
    33kV network side
    66kV network side
    My simple knowledge is that the neutral CT senses the I0 current which is the zero sequence current
    and since the transformer at 66kV side is Delta connection thus the earth fault relay will not since faults at the 66kV network
    Your valuable assist is highly appreciated
    الملفات المرفقة الملفات المرفقة
    • نوع الملف: doc Doc2.doc‏ (36.5 كيلوبايت, 53 مشاهدات)

  2. #2
    عضو مجلس إدارة المنتديات الصورة الرمزية Shaltoot
    تاريخ التسجيل
    Feb 2006
    الدولة
    EGYPT
    المشاركات
    223

    رد: Simple question

    اقتباس المشاركة الأصلية كتبت بواسطة tamerelminshawy مشاهدة المشاركة
    السلام عليكم ورحمة الله وبركاته
    Dear brothers
    I know that my question is simple but sometimes we might forget some principles
    In the attached file you will find a 66 33kV transfromer withDyn11 vector group
    the earth fault protection relay is connected to the CT installed on the transformer neutral point
    My simple inquiry is what will be the reaction of the earth fault relay in case of earth faults on
    33kV network side
    66kV network side
    My simple knowledge is that the neutral CT senses the I0 current which is the zero sequence current
    and since the transformer at 66kV side is Delta connection thus the earth fault relay will not since faults at the 66kV network
    Your valuable assist is highly appreciated


    Dear Tamer,

    I think your transformer has two complementary protections
    a- Differential protection which is to take care of the delta side earth faults (ANSI87
    b- restricted earth fault protection which is to take care of the earth faults on the star side (ANSI 50REF

    the answer to your question is no. the 33kV neutral point will only circultae earth current on the star side because the equivalent zero sequence impedance of the Dy transformer is opened from the delta side

  3. #3
    عضو فى رابطة مهندسى الكهرباء العرب الصورة الرمزية tamerelminshawy
    تاريخ التسجيل
    Apr 2006
    الدولة
    Saudi arabia
    المشاركات
    225

    رد: Simple question

    السلام عليكم ورحمة الله وبركاته
    DEAR Eng Hany
    Thank you for your response
    [As I understood from your reply the relay will react only in case the earth fault is at the star side and will not react if the fault is at the Delta side Is this correct
    Regarding the ANSI 87 and 50REF protection
    With my limited knowledge I know that both will provide protection for faults within the transformer winding zones and not for faults beyond the transformer

  4. #4
    عضو مجلس إدارة المنتديات الصورة الرمزية Shaltoot
    تاريخ التسجيل
    Feb 2006
    الدولة
    EGYPT
    المشاركات
    223

    رد: Simple question

    اقتباس المشاركة الأصلية كتبت بواسطة tamerelminshawy مشاهدة المشاركة
    السلام عليكم ورحمة الله وبركاته
    DEAR Eng Hany
    Thank you for your response
    [As I understood from your reply the relay will react only in case the earth fault is at the star side and will not react if the fault is at the Delta side Is this correct
    Regarding the ANSI 87 and 50REF protection
    With my limited knowledge I know that both will provide protection for faults within the transformer winding zones and not for faults beyond the transformer
    Dear Eng. Tamer

    Yes the relay will react only to earth faults returning from the star side

    Any fault on the 66kVside will be seen on the star point of the 220/66kv transformer

    Also to answer to your question, yes the 50REF and 87 functions are for faults within the transformer zone of protection. In this size of transformer there is no point to trip for faults outside the transformer zone because this should be taken care of with outgoing feeders. I don't recommend backup earth fault protection on this size of transformers

    my best regards

  5. #5
    عضو فى رابطة مهندسى الكهرباء العرب الصورة الرمزية tamerelminshawy
    تاريخ التسجيل
    Apr 2006
    الدولة
    Saudi arabia
    المشاركات
    225

    رد: Simple question

    السلام عليكم ورحمة الله وبركاته
    Dear Eng Hani
    I do not know how ever I could reward your Kindness
    So kindly accept my thanks and regards
    and I hope that you would allow me to ask one more question
    If we used residually connected earth fault relay at the delta side which is the 66kV side
    would this be enough to sense earth fault currents in the delta side of the transformer
    and to added residual voltage signal in order to make it react only in case of faults in 66kV side only
    I know that my questions are becoming more and more boring but I know that your Kindness will make you patient
    Best regards

  6. #6
    عضو مجلس إدارة المنتديات الصورة الرمزية Shaltoot
    تاريخ التسجيل
    Feb 2006
    الدولة
    EGYPT
    المشاركات
    223

    رد: Simple question

    اقتباس المشاركة الأصلية كتبت بواسطة tamerelminshawy مشاهدة المشاركة
    السلام عليكم ورحمة الله وبركاته
    Dear Eng Hani
    I do not know how ever I could reward your Kindness
    So kindly accept my thanks and regards
    and I hope that you would allow me to ask one more question
    If we used residually connected earth fault relay at the delta side which is the 66kV side
    would this be enough to sense earth fault currents in the delta side of the transformer
    and to added residual voltage signal in order to make it react only in case of faults in 66kV side only
    I know that my questions are becoming more and more boring but I know that your Kindness will make you patient
    Best regards
    I don't recommend residual current sensing from Phase CT summation because this type of protection is very poor because of the following
    a- It can't be set to below 15% of CT primary current to prevent false tripping due to saturation errors during through faults and inrush
    b- It will not detect turn to turn faults

    Differential protection is the only correct method to be used for this expensive equipment

    The protection must be complemented by a Sudden Pressure relay SPR which is very sensitive and very quick in detecting sudden increase in pressure due to turn to turn arcing

    My best regards

  7. #7
    عضو فى رابطة مهندسى الكهرباء العرب الصورة الرمزية tamerelminshawy
    تاريخ التسجيل
    Apr 2006
    الدولة
    Saudi arabia
    المشاركات
    225

    رد: Simple question

    السلام عليكم ورحمة الله وبركاته
    Dear Eng Hani
    No words can ever pay back your kindness, the only thing I can say
    لك جزيل الشكر والإحترام والتقدير اخى الكريـــــــــــــــــــــــــــــــــــ ـــــــــــــــــــــــــــــم
    بارك الله فيك وغفر لك وجــــــــــــــــزاك خـيـــــــــــــــــــــــــــــــــــــ ـــــــــــــــــــــــــراً،،

  8. #8
    عضو فى جمعية مهندسى الحماية الكهربائية الصورة الرمزية محمد شلهوب
    تاريخ التسجيل
    Jun 2006
    الدولة
    ksa
    المشاركات
    199

    رد: Simple question

    an other way to get earth refference point in delta side is

    Zigzag transformer

    you can read here

    http://en.wikipedia.org/wiki/Zigzag_transformer

  9. #9
    Junior Engineer الصورة الرمزية asadmalik
    تاريخ التسجيل
    Mar 2007
    الدولة
    Pakistan
    المشاركات
    4

    Re: Simple question

    How to select the NGR for 15MVA trafo 11/6.9 kv %Z=8%, DYn11, with OLTC . Whther 1000 Amp near to rated Amp is suitable or we go for low value 400Amp . Also is there any alarm / monitoring relay required for NGR

معلومات الموضوع

الأعضاء الذين يشاهدون هذا الموضوع

الذين يشاهدون الموضوع الآن: 1 (0 من الأعضاء و 1 زائر)

المواضيع المتشابهه

  1. a very simple a.c motor
    بواسطة م. كامل بدرخان في المنتدى قسم المحركات الكهربية و دوائر التحكم المبرمج PLC
    مشاركات: 7
    آخر مشاركة: 04-08-12, 02:11 PM
  2. plc simple examples
    بواسطة ضرار محمد في المنتدى قسم المحركات الكهربية و دوائر التحكم المبرمج PLC
    مشاركات: 4
    آخر مشاركة: 24-04-10, 01:13 PM
  3. Simple calculation_Short Circuit
    بواسطة Waleed tag في المنتدى قسم التصميم Design Department
    مشاركات: 12
    آخر مشاركة: 01-11-09, 08:48 PM
  4. PLC simple
    بواسطة Eng. mohannad hasan في المنتدى قسم المحركات الكهربية و دوائر التحكم المبرمج PLC
    مشاركات: 4
    آخر مشاركة: 27-08-09, 06:16 AM
  5. A simple way to learn PLC
    بواسطة mohamed medhat في المنتدى قسم المحركات الكهربية و دوائر التحكم المبرمج PLC
    مشاركات: 1
    آخر مشاركة: 10-10-07, 08:44 AM

الكلمات الدلالية لهذا الموضوع

المفضلات

المفضلات

ضوابط المشاركة

  • لا تستطيع إضافة مواضيع جديدة
  • لا تستطيع الرد على المواضيع
  • لا تستطيع إرفاق ملفات
  • لا تستطيع تعديل مشاركاتك
  •  
 

 

 

Flag Counter