    Generator Loss of Excitation Relay (40G).


    Electrical Generator Protection Relays.

    Electrical Generator is the main source of Electricity at Power Plant, we should make a many methods to protect the Generator from any faults can happen while Operation.
    The next figure shows the main single line diagram and Protection Scheme for the Generator.
    The Generator made by Mitsubishi Heavy Industries (MHI) and its specification as follows:

    Power-------------- 440 MVA
    Power Factor----- 0.85 lag
    Line Voltage------ 19 KV
    Frequency--------50HZ
    Speed-------------- 3000 rpm
    Hydrogen (H2) Gas Cooled @ 4.5 barg.



    Generator Loss of Excitation Relay (40G).

    If a Synchronous machine losses the Excitation, the following condition will occur:

    -When partial or complete loss of Excitation occurs on a synchronous generator, Reactive power flows from the other generator into the generator.

    -The KW is controlled by the Prime-Mover input, while KVAR output is controlled by the Field Excitation. If the system is large enough to supply the deficiency in Excitation through the armature, the synchronous generator will operate as an induction generator, supplying essentially the same KW to the system as before the loss of Excitation.

    -Since Synchronous generator is not designed for asynchronous operation, the machine output will oscillate slightly as the rotor oscillates in an attempt to lock into synchronism.

    -Loss of Synchronism does not require immediate tripping unless there is an accompanying decrease in the terminal voltage that threatens system stability; it generally takes at least 2 to 6 Sec. to lose synchronism.


    Data for setting calculations.
    Generator capacity-------440000KVA
    Generator Voltage--------19KVA
    CT turns ratio-------------18000/5=3600
    VT turns ration-----------19000/100=190
    Gen. Transient impedance--------Xd’=24.8%
    Gen. Synchronous impedance----Xd=195%

    Relay setting calculations.
    Relay Side Impedance
    Z=Z% * ((KV2 * 10)/KVA) * (CT ratio/VT ratio)


    Setting of small circle.
    1-Circle #1 Diameter
    Z=100 *((192*10)/440000)*(3600/190) = 15.55 Ω

    2-Circle #1 Offset
    Z=24.8 *((192*10)/440000)*(3600/190) = 1.93 Ω

    3-Circle #1 Diameter
    Setting=15 Cycles (0.3 Sec.)



    Setting of large circle.
    1-Circle #2 Diameter
    Z=195 *((192*10)/440000)*(3600/190) = 30.31 Ω

    2-Circle #2 Offset
    Z=24.8 *((192*10)/440000)*(3600/190) = 1.93 Ω

    3-Circle #1 Diameter
    Setting=75 Cycles (1.5 Sec.)



    الصور المرفقة الصور المرفقة

معلومات الموضوع

الأعضاء الذين يشاهدون هذا الموضوع

الذين يشاهدون الموضوع الآن: 1 (0 من الأعضاء و 1 زائر)

المواضيع المتشابهه

  1. ماهو دور Excitation في Generator ?
    بواسطة alshammari في المنتدى قسم محطات التوليد و أنظمة التشغيل و التحكم Power Plants
    مشاركات: 13
    آخر مشاركة: 06-01-14, 09:26 PM
  2. Generator Protection against Loss of Excitation
    بواسطة المنذر عبد الله في المنتدى محاضرات و دروس فى هندسة الوقاية الكهربائية
    مشاركات: 2
    آخر مشاركة: 22-12-12, 08:54 AM
  3. كتاب جميل Loss-of-excitation Protection for Synchronous Generators
    بواسطة ahmed ghanem في المنتدى قسم محطات التوليد و أنظمة التشغيل و التحكم Power Plants
    مشاركات: 4
    آخر مشاركة: 13-08-10, 09:13 PM
  4. Loss-of-excitation Protection for Synchronous Generators
    بواسطة Mohamed Abd Raboh في المنتدى قسم وقاية نظم القوى الكهربائية Power System Protection
    مشاركات: 1
    آخر مشاركة: 17-10-07, 05:24 AM
  5. loss of excitation protection
    بواسطة abdelkarim في المنتدى قسم محطات التوليد و أنظمة التشغيل و التحكم Power Plants
    مشاركات: 0
    آخر مشاركة: 16-01-07, 09:39 AM

المفضلات

المفضلات

ضوابط المشاركة

  • لا تستطيع إضافة مواضيع جديدة
  • لا تستطيع الرد على المواضيع
  • لا تستطيع إرفاق ملفات
  • لا تستطيع تعديل مشاركاتك
  •