    هل تعلم ماهو معامل k factor للمحولات ادخل وستعرف

    Transformer K- Factor

    What is a K-factor?
    It is a value used to determine how much harmonic current a transformer can handle without exceeding it’s maximum temperature rise level. K-factor values range from 1 to 50. K-factor of 1 is used for linear loads only, and a K-factor of 50 is used for the harshest harmonic environment possible.
    A K-factor of 13 is typical. When transformers use a K-factor value, they are said to be K-rated.
    A K-rated transformer is one which is used to deal with harmonic generating loads. Harmonics generate additional heat in the transformer and cause non-K-rated transformers to overheat possibly causing a fire, also reducing the life of the transformer. K-rated transformers are sized appropriately to handle this additional heat and tested to UL 1561 rigid standards for K-factor rated transformers. The way a K-rated transformer works is it uses a double sized neutral conductor and either change the geometry of their conductors or use multiple conductors for the coils. Quality transformers are manufactured with high grade silicon steel, copper windings, and more air ducts.
    The use of a K-rated transformer is anywhere non-linear loads are present. Prime uses would be in factory automation, computer rooms, and office buildings because of the high harmonic ******* in these areas. Typically a K-13 rated transformer is sufficient for most applications. Loads approaching 1005 non-linear or more Than 75% THD should incorporate a K-20 rated transformer.
    Over the past several years there has been dramatic growth in the use of equipment incorporating switching type power supplies. Examples are personal computers, video display terminals, fax machines, copiers, electronic high efficiency ballasts, UPS systems, variable speed drives and various medical electronic monitors. The nature of all these loads is non-linear; they only demand current during part of the cycle and/or change their impedance during the voltage cycle. This type of load creates harmonic currents, which in turn generate heat in the distribution equipment, neutral conductors and distribution transformers.
    Underwriters Laboratories (UL) has designated K-factor as a means of rating a transformers ability to handle loads which generate harmonic currents, UL recognizes K-factor values of 4, 9, 13, 20, 30, 40 and 50. The K-factor ratings are based on information contained in ANSI/IEEE C57.110-1986, Recommended Practice for Establishing Capability When Supplying Nonsinusoidal Load Currents. The K-factor number tells us how much a transformer must be de-rated to handle a definite non-linear load or, conversely, how much it must be oversized to handle the same load.

    The following rules will generally result in an acceptable choice of K-factor value:
    1. Follow successful past practice in sizing the transformer.
    2. Where the harmonic current producing equipment is less than 15 per cent, use a standard transformer.
    3. Where the electronic equipment represents up to 35 per cent of the load, use a K-4 rated transformer.
    4. Where the electronic equipment represents up to 75 per cent of the load, use a K-13 rated transformer.
    5. Where 100 per cent of the load is electronic equipment, use a K-20 rated transformer.
    6. Higher K-factor ratings are generally reserved for specific pieces of equipment where the harmonic spectrum of the load is known.
    K-rating is a heat survival rating, not a treatment of associated power quality issues like voltage distortion, and efficiency isn’t typically discussed. Surviving the extra heat means using more core and coil material, and sometimes use of different construction techniques. Depending on the manufacturer’s design, harmonic losses may be reduced to varying degrees. Ironically, even though the designated use of the K-rated transformer is to feed nonlinear load, manufacturers publish their loss data under linear load conditions.


    لا اله الا الله محمد رسول الله
    علها نحيا وعليها نموت*** وبها نبعث يوم القيامة


  2. #2
    Junior Engineer الصورة الرمزية محمد عبد الفتاح المصرى
    تاريخ التسجيل
    Dec 2008
    الدولة
    مصر
    المشاركات
    229

    رد: هل تعلم ماهو معامل k factor للمحولات ادخل وستعرف

    مشكور اخى على المعلومه

  3. #3
    Junior Engineer الصورة الرمزية mahmoudali
    تاريخ التسجيل
    Sep 2008
    الدولة
    cairo
    المشاركات
    20

    Re: هل تعلم ماهو معامل k factor للمحولات ادخل وستعرف

    جزاك الله خيرا

  4. #4
    Junior Engineer الصورة الرمزية Ahmed Fathi ismail
    تاريخ التسجيل
    Jun 2010
    الدولة
    Egypt,Cairo
    المشاركات
    13

    رد: هل تعلم ماهو معامل k factor للمحولات ادخل وستعرف

    شكــــــــــــــــــــــــــــــــــــــ ــــــــــــــــــــــــــــــــراً

  5. #5
    Junior Engineer الصورة الرمزية حسن اتيم
    تاريخ التسجيل
    Sep 2015
    الدولة
    sudan
    المشاركات
    3

    رد: Re: هل تعلم ماهو معامل k factor للمحولات ادخل وستعرف

    شكرا جزيلا علي المعلومة

  6. #6
    Junior Engineer الصورة الرمزية محمود الجناينى
    تاريخ التسجيل
    Aug 2006
    الدولة
    مصر
    المشاركات
    131

    رد: هل تعلم ماهو معامل k factor للمحولات ادخل وستعرف

    جزاك الله خيرا

  7. #7
    Junior Engineer
    تاريخ التسجيل
    Jun 2013
    الدولة
    بغداد
    المشاركات
    35

    رد: هل تعلم ماهو معامل k factor للمحولات ادخل وستعرف

    باختصار صديقي وبعيدا عن التفاصيل ( ممكن البحث عن التفاصيل بعد ان نفهم الفكرة ولايهم باي لغه ) فان k factor يحدد قابلية المحوله على العمل في شبكة كهربائيه اعتمادا على مقدار الهارمونيك الناشيء في هذه الشبكة
    >
    الملفات المرفقة الملفات المرفقة

  8. #8
    Junior Engineer الصورة الرمزية مهندس احمد رمضان ساك
    تاريخ التسجيل
    Feb 2012
    الدولة
    جده
    المشاركات
    102

    رد: هل تعلم ماهو معامل k factor للمحولات ادخل وستعرف

    جزاك الله كل خير

معلومات الموضوع

الأعضاء الذين يشاهدون هذا الموضوع

الذين يشاهدون الموضوع الآن: 1 (0 من الأعضاء و 1 زائر)

المواضيع المتشابهه

  1. ماهو tan delta test للمحولات
    بواسطة مجتبى عبدالعليم عبدالله في المنتدى قسم هندسة المحولات الكهربية Electrical Transformer
    مشاركات: 11
    آخر مشاركة: 25-10-14, 11:24 PM
  2. ماهو الgrouping factor&dearting factor هااااااااام
    بواسطة احمد محمد السيد بيومي في المنتدى قسم التصميم Design Department
    مشاركات: 4
    آخر مشاركة: 26-09-10, 08:41 PM
  3. ماهو tan delta test للمحولات
    بواسطة مجتبى عبدالعليم عبدالله في المنتدى قسم وقاية نظم القوى الكهربائية Power System Protection
    مشاركات: 0
    آخر مشاركة: 11-05-10, 10:20 AM
  4. هل تعلم ؟ (ج1) >>>> ادخل
    بواسطة Oday Husham في المنتدى نادى المهندسين
    مشاركات: 1
    آخر مشاركة: 19-12-08, 08:29 PM
  5. تحسين معامل القدرة للمحولات
    بواسطة حازم خالد في المنتدى قسم الموضوعات العامة
    مشاركات: 2
    آخر مشاركة: 02-01-06, 12:19 PM

المفضلات

المفضلات

ضوابط المشاركة

  • لا تستطيع إضافة مواضيع جديدة
  • لا تستطيع الرد على المواضيع
  • لا تستطيع إرفاق ملفات
  • لا تستطيع تعديل مشاركاتك
  •  

 

 

Flag Counter