Detection of Oil-Pressboard Insulation Aging with Dielectric Spectroscopy in Time and Frequency Domain Measurements
Omar Hassan1*, A. A. Shyegani2, Hossein Borsi2, Ernst Gockenbach2 E. M. Abu-Elzahab3
M. I. Gilany3
1Department of High Voltage Networks, High Institute of Energy, Aswan, Egypt
2Institute of Electric Power Systems, Schering-Institut, University of Hannover, Germany
3Department of Electric Power and Machines, Faculty of Engineering, Cairo University, Giza, Egypt E-mail : ons_hassan@yahoo.com
Abstract:
The insulation system of power transformers consists of oil and cellulose, whose dielectric properties are strongly influenced by moisture, temperature and aging.
Their condition can therefore, be evaluated using dielectric response measurements.
This contribution describes the Return Voltage Measurement (RVM) diagnostic method based on scanning the polarization spectra of the oil-paper insulation in the time range of 1s to 1200s at an excitation voltage of 500V (DC).
The variation of the dissipation factor (tan δ) and power factor (cos θ) in the
frequency range of 0.0001 to 1000 Hz were measured and the effects of moisture and aging were analyzed.
Furthermore accelerated aging processes of oil-paper samples were investigated under air environment up to a temperature of 388 K (115°C).
Typical transformer proportions of copper, aluminum, zinc and iron were added to oil-paper insulation during the aging process in order to simulate the possible oxidation processes.
For the investigation of the long time behavior, the oil-paper insulation samples were aged at different aging times at 250, 500, 1000 and 2000 hours which simulate long time service condition due to the used severe aging conditions.
For more detail you can down load attachment file (complete paper)