    Al salam alaykom wa rahmat allah
    Respectid Sir
    Your advice and directions are highly appreciated in the subject mentioned below:
    We completed the installation of a 9*2MVA low tension paralleled operatoin generatioin plant and is required to be tested and commissioned.
    The total load on the generators (up to now) is nearly 6 MVA.
    -any suggestion about testing and commissioning for the mentioned plant?
    -What are the procedure for testing the generators to be tested individually and through parallel operation?
    -What are the steps for loading gnerators and the duration for loading , and any idea about overload test?
    your help will be highly appreciated.
    Thanks and regards.

    Hani M. Saeed

  2. #2
    عضو مجلس إدارة المنتديات
    تاريخ التسجيل
    Sep 2006
    الدولة
    Ciro
    المشاركات
    277

    Exclamation رد: requiered test procedure for low tension power plant

    اقتباس المشاركة الأصلية كتبت بواسطة hani51 مشاهدة المشاركة
    Al salam alaykom wa rahmat allah
    Respectid Sir
    Your advice and directions are highly appreciated in the subject mentioned below:
    We completed the installation of a 9*2MVA low tension paralleled operatoin generatioin plant and is required to be tested and commissioned.
    The total load on the generators (up to now) is nearly 6 MVA.
    -any suggestion about testing and commissioning for the mentioned plant?
    -What are the procedure for testing the generators to be tested individually and through parallel operation?
    -What are the steps for loading gnerators and the duration for loading , and any idea about overload test?
    your help will be highly appreciated.
    Thanks and regards.

    Hani M. Saeed
    Dear Engineer/Hany

    (The total load on the generators (up to now) is nearly 6 MVA.)
    that is meaning that the gnerators now in services!!!!!!
    How you are loading this gnerators
    befor commissioning and tested?????
    OKY,can you send to us the system & the type of these gnerators& the test equipment you have???

    - best regards
    Mohamed Gamal Edeen

  3. #3
    عضو فى مجلس إدارة المنتديات الصورة الرمزية hani51
    تاريخ التسجيل
    Mar 2006
    الدولة
    sharjah
    المشاركات
    1,494

    رد: requiered test procedure for low tension power plant

    al salam alaykom wa rahmat allah
    Thank you so much for your kind reply
    actually as i understand from the engineer involved in the site(a close freind of me) that the generators are going to feed the new installations which is now under construction and the total load is as mentioned before nearly 6MVA.
    The important thing is that the generators istallations is completed and required to be tested and commissioned, so we want the suitable procedure to test the generators, without using the load of the site if possible, otherwise we have to arrange the load to be used for testing procedure. .

  4. #4
    عضو فى رابطة مهندسى الكهرباء العرب
    تاريخ التسجيل
    Dec 2005
    الدولة
    Palestine
    المشاركات
    110

    رد: requiered test procedure for low tension power plant

    بعد التحية

    أولا : نريد معرفة prime mover الخاص بالمولد
    ثانيا:Tech.Data
    ثانيا: فيما يلي الفحوصات التقليدية للمولدات


    1- AVR regulator setting and adjusting in stand still condition with the generator running at no load
    2- Overspeed protection

    3- Open and short circuit test on the generator
    4-Stator earth fault
    5-generator transformer overcurent and earth fault
    6-negative sequence current
    7-Differential relay
    طريقة الفحص:
    الهدف من الفحص هو إعطاء إشارة إلى ملف Trip الخاص بالمولد ليفصل
    ويتم من خلال injection أو من خلال jumper
    هذه بعض الفحوصلت التقليدية التي أعرفها وأتمنى تزويدنا حتى نتمكن من مساعدتك قدر الإمكان بإذن الله

معلومات الموضوع

الأعضاء الذين يشاهدون هذا الموضوع

الذين يشاهدون الموضوع الآن: 1 (0 من الأعضاء و 1 زائر)

المواضيع المتشابهه

  1. Areva Test Procedure and Test format
    بواسطة ESSAM ALBANNA في المنتدى قسم وقاية نظم القوى الكهربائية Power System Protection
    مشاركات: 14
    آخر مشاركة: 20-09-15, 12:47 PM
  2. 7UT612 Transformer DIFF test format with test procedure
    بواسطة ENG.Mohamed shokry في المنتدى قسم الوقاية التفاضلية Differential Protection
    مشاركات: 27
    آخر مشاركة: 20-09-15, 12:41 PM
  3. 33 kv bus bar test procedure
    بواسطة ali abualsamen في المنتدى قسم هندسة الجهد العالى High voltage engineering
    مشاركات: 0
    آخر مشاركة: 25-12-12, 04:09 PM
  4. Site test procedure for power cables 380KV
    بواسطة م. حمدي محمد في المنتدى قسم نقل وتوزيع الطاقه باستخدام الكابلات الأرضية under ground cable
    مشاركات: 12
    آخر مشاركة: 11-10-11, 06:58 PM
  5. DEF REL 505 TEST PROCEDURE
    بواسطة AHMED SHENAWY في المنتدى قسم وقاية نظم القوى الكهربائية Power System Protection
    مشاركات: 2
    آخر مشاركة: 05-05-10, 08:09 PM

الكلمات الدلالية لهذا الموضوع

المفضلات

المفضلات

ضوابط المشاركة

  • لا تستطيع إضافة مواضيع جديدة
  • لا تستطيع الرد على المواضيع
  • لا تستطيع إرفاق ملفات
  • لا تستطيع تعديل مشاركاتك
  •  
 

 

 

Flag Counter