    I urgently need your support

    السلام عليكم ورحمة الله وبركاته

    السلام عليكم ورحمة الله وبركاته

    Two generators 10.5 kV each on is connected to a bus bar(33 kV) through block delta/star transformer 10.5 / 33 kv
    with the 33kV side star and earthed through 250 ohm
    we have two circuit breakers installed at the 10.5 and 33 kV sides
    One generator was in operation (i.e 10.5 and 33 kV breakers closed) and producing 40MW.
    The other generator was in stand by (10.5 kV breaker opened while 33kV breaker closed)
    An earth fault occured on the busbar and the in operation Generator sensed the fault through directional earth fault relay installed at the 33 kV side (C.T and V.T of the relay are installed at the 33kV side) and tripped the 33 and 10.5 breakers.
    The question is: Why for the stand by generator, also sensed the fault and tripped the 33kV breaker, when it was not in operation and did not feed the fault
    please explain if this have a relation to the fact that the block transformer at the 33kV side is star and earthed.

    الملفات المرفقة الملفات المرفقة
    • نوع الملف: doc Doc1.doc‏ (60.0 كيلوبايت, 30 مشاهدات)

  2. #2
    عضو مجلس إدارة المنتديات الصورة الرمزية Shaltoot
    تاريخ التسجيل
    Feb 2006
    الدولة
    EGYPT
    المشاركات
    223

    مشاركة: I urgently need your support

    If the fault occured on the 33kV side while only one generator was in operation then this is a forward earth fault (not reverse) accordingly the 51N relay should operate instead of the 67N relay

    acccordingly there must be inter-tripping between the two parallel 33kV circuit breakers and both should trip because the fault is forward

  3. #3
    V.I.P Member الصورة الرمزية عامر محمد شنتير
    تاريخ التسجيل
    Jun 2006
    الدولة
    فلسطين
    المشاركات
    283

    مشاركة: I urgently need your support

    ممكن عربي :01s4:

  4. #4
    عضو فى رابطة مهندسى الكهرباء العرب الصورة الرمزية tamerelminshawy
    تاريخ التسجيل
    Apr 2006
    الدولة
    Saudi arabia
    المشاركات
    225

    مشاركة: I urgently need your support

    Dear Eng. Shaltoot.
    My deep appreciation for your valuable comment. The relay for restricted earth fault F22 in the drawing is set to protect the generator,transformer block that means that the forward direction is not when current flows to the 33kV bus but the forward direction is when current flows from the 33kV down wards to the 10.5kV. Thus I think the for the generator in operation the relay should not has tripped as the current flowed to the 33kV bar and for the stand by generator since the transformer 33kV side is star and earthed. then a part of the earth fault current will flow to the transformer earthing and thus it tripped

  5. #5
    عضو مجلس إدارة المنتديات الصورة الرمزية Shaltoot
    تاريخ التسجيل
    Feb 2006
    الدولة
    EGYPT
    المشاركات
    223

    مشاركة: I urgently need your support

    اقتباس المشاركة الأصلية كتبت بواسطة tamerelminshawy
    Dear Eng. Shaltoot.
    My deep appreciation for your valuable comment. The relay for restricted earth fault F22 in the drawing is set to protect the generator,transformer block that means that the forward direction is not when current flows to the 33kV bus but the forward direction is when current flows from the 33kV down wards to the 10.5kV. Thus I think the for the generator in operation the relay should not has tripped as the current flowed to the 33kV bar and for the stand by generator since the transformer 33kV side is star and earthed. then a part of the earth fault current will flow to the transformer earthing and thus it tripped
    Forward direction is the normal flow of current which is from 10.5kV to 33kV. call me at Schneider Egypt if you need assistance

معلومات الموضوع

الأعضاء الذين يشاهدون هذا الموضوع

الذين يشاهدون الموضوع الآن: 1 (0 من الأعضاء و 1 زائر)

المواضيع المتشابهه

  1. برنامج omron NT support tool
    بواسطة Mahmoud Abd Elhameed في المنتدى PLC type OMRON
    مشاركات: 1
    آخر مشاركة: 12-12-10, 11:16 AM
  2. IEC 61131-3 programming environment provides support
    بواسطة walid issa في المنتدى قسم المحركات الكهربية و دوائر التحكم المبرمج PLC
    مشاركات: 0
    آخر مشاركة: 23-07-10, 04:54 PM
  3. Cable Support System - OBO Bettermann
    بواسطة Youssef Mohamed في المنتدى قسم نقل وتوزيع الطاقه باستخدام الكابلات الأرضية under ground cable
    مشاركات: 4
    آخر مشاركة: 08-04-10, 05:15 AM
  4. urgent ineed your support
    بواسطة محمد الحمدلله في المنتدى قسم المحركات الكهربية و دوائر التحكم المبرمج PLC
    مشاركات: 2
    آخر مشاركة: 22-04-08, 06:04 PM
  5. Distributed Generation as Voltage Support for Single
    بواسطة حسن الابيارى في المنتدى قسم وقاية نظم القوى الكهربائية Power System Protection
    مشاركات: 0
    آخر مشاركة: 21-10-07, 10:19 AM

الكلمات الدلالية لهذا الموضوع

المفضلات

المفضلات

ضوابط المشاركة

  • لا تستطيع إضافة مواضيع جديدة
  • لا تستطيع الرد على المواضيع
  • لا تستطيع إرفاق ملفات
  • لا تستطيع تعديل مشاركاتك
  •  
 

 

 

Flag Counter