الموضوع: actual directional earth fault relay connection

  1. #1
    عضو فى رابطة مهندسى الكهرباء العرب الصورة الرمزية tamerelminshawy
    تاريخ التسجيل
    Apr 2006
    الدولة
    Saudi arabia
    المشاركات
    225

    actual directional earth fault relay connection

    السلام عليكم ورحمة الله وبركاته
    Dear brothers
    Attached file shows actual wiring for directional earth fault protection relay.
    This relay is set to trip in the forward direction with V, I angle = 15
    according to the wiring you will see that the earthing point of the C.T secondary is towards the transformer. This as far as I know means that the forward direction is when the earth fault current follows towards the transformer.
    I hope that you will find this usefull and I hope to receive your comments

    My deep regards to you all
    الملفات المرفقة الملفات المرفقة

  2. #2
    عضو مجلس إدارة المنتديات الصورة الرمزية Shaltoot
    تاريخ التسجيل
    Feb 2006
    الدولة
    EGYPT
    المشاركات
    223

    مشاركة: actual directional earth fault relay connection

    اقتباس المشاركة الأصلية كتبت بواسطة tamerelminshawy
    السلام عليكم ورحمة الله وبركاته
    Dear brothers
    Attached file shows actual wiring for directional earth fault protection relay.
    This relay is set to trip in the forward direction with V, I angle = 15
    according to the wiring you will see that the earthing point of the C.T secondary is towards the transformer. This as far as I know means that the forward direction is when the earth fault current follows towards the transformer.
    I hope that you will find this usefull and I hope to receive your comments

    My deep regards to you all

    The point of earthing has no significance

    What determine the forward direction of the CT is the location of P1 and P2 (P1 is usually marked by a black dot on the window CT

    The forward direction is when the current flows from P1 to P2 marks

    Accordingly the relay must be connected to S1 and S2 respectively

    By the way most modern digital relays have an internal setting ( LOAD/SOURCE

  3. #3
    عضو فى رابطة مهندسى الكهرباء العرب الصورة الرمزية tamerelminshawy
    تاريخ التسجيل
    Apr 2006
    الدولة
    Saudi arabia
    المشاركات
    225

    مشاركة: actual directional earth fault relay connection

    اقتباس المشاركة الأصلية كتبت بواسطة Shaltoot
    The point of earthing has no significance

    What determine the forward direction of the CT is the location of P1 and P2 (P1 is usually marked by a black dot on the window CT

    The forward direction is when the current flows from P1 to P2 marks

    Accordingly the relay must be connected to S1 and S2 respectively

    By the way most modern digital relays have an internal setting ( LOAD/SOURCE
    Dear Eng. Shaltoot
    Many thanks to your valuable comments and I amy sorry that I caused you much trouble
    According to the wiring K point on the C.T primary is connected to the 33 kV side and the L point is connected to the 10.5 kV side.
    and since the protection relay is adjusted to trip in the forward direction then it will trip when fault current flows from the 33kV side downwards to the 10.5 kV


معلومات الموضوع

الأعضاء الذين يشاهدون هذا الموضوع

الذين يشاهدون الموضوع الآن: 1 (0 من الأعضاء و 1 زائر)

المواضيع المتشابهه

  1. ملف رائع من اريفا يشرح Directional overcurrent&earth fault
    بواسطة Eng_Mhagag في المنتدى محاضرات و دروس فى هندسة الوقاية الكهربائية
    مشاركات: 29
    آخر مشاركة: 28-01-19, 11:05 AM
  2. testing directional earth fault for sepam relay
    بواسطة ahmed maghawry في المنتدى قسم الأختبارت و الفحص الفنى Technical test and insepection
    مشاركات: 6
    آخر مشاركة: 29-06-14, 09:55 PM
  3. earth fault relay
    بواسطة محمد السيد إبراهيم في المنتدى قسم وقاية نظم القوى الكهربائية Power System Protection
    مشاركات: 0
    آخر مشاركة: 17-03-13, 01:31 AM
  4. Test Sheet المعتمد في العراق لفحص Directional Earth Fault
    بواسطة bashar sabeeh في المنتدى قسم الأختبارت و الفحص الفنى Technical test and insepection
    مشاركات: 7
    آخر مشاركة: 20-11-11, 10:12 PM
  5. VAMP140-Over Current and earth fault relay
    بواسطة م.هشام رمضان في المنتدى قسم كتالوجات أجهزة الوقاية
    مشاركات: 2
    آخر مشاركة: 15-06-06, 08:17 AM

الكلمات الدلالية لهذا الموضوع

المفضلات

المفضلات

ضوابط المشاركة

  • لا تستطيع إضافة مواضيع جديدة
  • لا تستطيع الرد على المواضيع
  • لا تستطيع إرفاق ملفات
  • لا تستطيع تعديل مشاركاتك
  •  
 

 

 

Flag Counter