    المعادلات الأساسية فى حسابات محولات القدرة

    [align=left]بسم الله الرحمن الرحيم
    الأخوة الأعزاء
    السلام عليكم و رحمة الله وبركات
    هذة هى المشاركة الاولى فى منتدى التصميم و نبدء بأذن الله بالتذكير بالحسابات الأولية فى تصميم المحولات الكهربية.

    محولات القدرة Transformers
    For an ideal two-winding transformer with primary voltage V1 applied across N1 primary turns and secondary voltage V2 appearing across N2 secondary turns:
    V1 / V2 = N1 / N2
    The primary current I1 and secondary current I2 are related by:
    I1 / I2 = N2 / N1 = V2 / V1

    For an ideal step-down auto-transformer with primary voltage V1 applied across (N1 + N2) primary turns and secondary voltage V2 appearing across N2 secondary turns:
    V1 / V2 = (N1 + N2) / N2
    The primary (input) current I1 and secondary (output) current I2 are related by:
    I1 / I2 = N2 / (N1 + N2) = V2 / V1
    Note that the winding current is I1 through the N1 section and (I2 - I1) through the N2 section.

    For a single-phase transformer with rated primary voltage V1, rated primary current I1, rated secondary voltage V2 and rated secondary current I2, the voltampere rating S is:
    S = V1I1 = V2I2

    For a balanced m-phase transformer with rated primary phase voltage V1, rated primary current I1, rated secondary phase voltage V2 and rated secondary current I2, the voltampere rating S is:
    S = mV1I1 = mV2I2

    The primary circuit impedance Z1 referred to the secondary circuit for an ideal transformer with N1 primary turns and N2 secondary turns is:
    Z12 = Z1(N2 / N1)2

    The secondary circuit impedance Z2 referred to the primary circuit for an ideal transformer with N1 primary turns and N2 secondary turns is:
    Z21 = Z2(N1 / N2)2

    The voltage regulation V2 of a transformer is the rise in secondary voltage which occurs when rated load is disconnected from the secondary with rated voltage applied to the primary. For a transformer with a secondary voltage E2 unloaded and V2 at rated load, the per-unit voltage regulation V2pu is:

    V2pu = (E2 - V2) / V2
    Note that the per-unit base voltage is usually V2 and not E2.
    Open Circuit Test
    If a transformer with its secondary open-circuited is energised at rated primary voltage, then the input power Poc represents the core loss (iron loss PFe) of the transformer:
    Poc = PFe

    The per-phase star values of the shunt magnetising admittance Ym, conductance Gm
    and susceptance Bm of an m-phase transformer are calculated from the open-circuit test results for the per-phase primary voltage V1oc, per-phase primary current I1oc and input power Poc using:
    Ym = I1oc / V1oc
    Gm = mV1oc2 / Poc
    Bm = (Ym2 - Gm2)½
    Short Circuit Test
    If a transformer with its secondary short-circuited is energised at a reduced primary voltage which causes rated secondary current to flow through the short-circuit, then the input power Psc represents the load loss (primary copper loss P1Cu, secondary copper loss P2Cu and stray loss Pstray) of the transformer:
    Psc = P1Cu + P2Cu + Pstray
    Note that the temperature rise should be allowed to stabilise because conductor

    resistance varies with temperature.
    If the resistance of each winding is determined by winding resistance tests immediately after the short circuit test, then the load loss of an m-phase transformer may be split into primary copper loss P1Cu, secondary copper loss P2Cu and stray loss Pstray:
    P1Cu = mI1sc2R1star
    P2Cu = mI2sc2R2star
    Pstray = Psc - P1Cu - P2Cu
    If the stray loss is neglected, the per-phase star values referred to the primary of the total series impedance Zs1, resistance Rs1 and reactance Xs1 of an m-phase transformer are calculated from the short-circuit test results for the per-phase primary voltage V1sc, per-phase primary current I1sc and input power Psc using:
    Zs1 = V1sc / I1sc = Z1 + Z2(N12 / N22)
    Rs1 = Psc / mI1sc2 = R1 + R2(N12 / N22)
    Xs1 = (Zs12 - Rs12)½ = X1 + X2(N12 / N22)
    where Z1, R1 and X1 are primary values and Z2, R2 and X2 are secondary values
    Winding Resistance Test
    The resistance of each winding is measured using a small direct current to avoid thermal and inductive effects. If a voltage Vdc causes current Idc to flow, then the resistance R is:
    R = Vdc / Idc
    If the winding under test is a fully connected balanced star or delta and the resistance measured between any two phases is Rtest, then the equivalent winding resistances Rstar or Rdelta are:
    Rstar = Rtest / 2
    Rdelta = 3Rtest / 2
    The per-phase star primary and secondary winding resistances R1star and R2star of an m-phase transformer may be used to calculate the separate primary and secondary copper losses P1Cu and P2Cu:
    P1Cu = mI12R1star
    P2Cu = mI22R2star
    Note that if the primary and secondary copper losses are equal, then the primary and secondary resistances R1star and R2star are related by:
    R1star / R2star = I22 / I12 = N12 / N22
    The primary and secondary winding resistances R1 and R2 may also be used to check the effect of stray loss on the total series resistance referred to the primary, Rs1, calculated from the short circuit test results:
    Rs1 = R1 + R2(N12 / N22 ][/align]ملحوظه هامة
    توجد بعض الرموز اليونانية المستخدمة فى الموضوع سوف تظهر فى صورة مربعات صغيرة نتيجة ان المتصفح لايدعم هذة الرموز حيث ان المتصفح يدعم نوع خط واحد فى الصفحة فقمت بوضع نفس المقال فى ملف مرفق يمكن تحميله من اسفل
    مع خالص تحياتى
    الملفات المرفقة الملفات المرفقة
    مهندس / سيد سعد

    رئيس مجلس الإدارة و المشرف العام
    على شبكة منتديات رابطة مهندسى الكهرباء العرب
    1 - منتديات نظم القوى الكهربائية و شبكات النقل
    2 -المنتدى العلمى لمهندسى الشركة المصرية لنقل الكهرباء


  2. #2
    V.I.P Member الصورة الرمزية mohammed_yasin
    تاريخ التسجيل
    Mar 2006
    الدولة
    Egypt
    المشاركات
    451

    مشاركة: المعادلات الأساسية فىحسابات محولات القدرة

    ملخص رائع المعادلات الأساسية فى حسابات محولات القدرة
    شكراً لك اخي الكريم

  3. #3
    Junior Engineer
    تاريخ التسجيل
    May 2006
    الدولة
    السعودية
    المشاركات
    14

    مشاركة: المعادلات الأساسية فىحسابات محولات القدرة

    اقتباس المشاركة الأصلية كتبت بواسطة mohammed_yasin
    ملخص رائع المعادلات الأساسية فى حسابات محولات القدرة
    شكراً لك اخي الكريم
    ملخص بسيط ورائع، حفظك الله أخي الكريم

  4. #4
    نائب رئيس مجلس الإدارة الصورة الرمزية ali yaghi
    تاريخ التسجيل
    Oct 2005
    الدولة
    UAE
    المشاركات
    1,669

    Wink مشاركة: المعادلات الأساسية فىحسابات محولات القدرة

    السلام عليكم ورحمة الله وبركاته
    أخي العزيز م.سيد سعد
    الف شكر على هذه المساهمة القيمة ونعدكم الأسبوع القادم بالتطرق الى موضوع المحولات فلدينا
    ان شاء الله مكتبة غنية بذلك...:01s2:

معلومات الموضوع

الأعضاء الذين يشاهدون هذا الموضوع

الذين يشاهدون الموضوع الآن: 1 (0 من الأعضاء و 1 زائر)

المواضيع المتشابهه

  1. المواد الأساسية المستخدمة بمحولات القدرة(درس 4)مع المهندس كريم الفخرانى
    بواسطة كريم محمد احمد الفخرانى في المنتدى قسم وقاية نظم القوى الكهربائية Power System Protection
    مشاركات: 0
    آخر مشاركة: 12-03-09, 08:40 PM
  2. المواد الأساسية المستخدمة بمحولات القدرة(درس 3مع المهندس كريم الفخرانى
    بواسطة كريم محمد احمد الفخرانى في المنتدى قسم وقاية نظم القوى الكهربائية Power System Protection
    مشاركات: 0
    آخر مشاركة: 12-03-09, 08:34 PM
  3. المواد الأساسية المستخدمة بمحولات القدرة(درس 2)مع المهندس كريم الفخرانى
    بواسطة كريم محمد احمد الفخرانى في المنتدى قسم وقاية نظم القوى الكهربائية Power System Protection
    مشاركات: 0
    آخر مشاركة: 12-03-09, 08:29 PM
  4. المواد الأساسية المستخدمة بمحولات القدرة(درس 1)مع المهندس كريم الفخرانى
    بواسطة كريم محمد احمد الفخرانى في المنتدى قسم وقاية نظم القوى الكهربائية Power System Protection
    مشاركات: 0
    آخر مشاركة: 12-03-09, 08:23 PM
  5. اطلب برنامج عن حسابات القدرة وغيرها في الinduction motor
    بواسطة محمد سعادة في المنتدى قسم المحركات الكهربية و دوائر التحكم المبرمج PLC
    مشاركات: 1
    آخر مشاركة: 30-10-07, 10:47 PM

الكلمات الدلالية لهذا الموضوع

المفضلات

المفضلات

ضوابط المشاركة

  • لا تستطيع إضافة مواضيع جديدة
  • لا تستطيع الرد على المواضيع
  • لا تستطيع إرفاق ملفات
  • لا تستطيع تعديل مشاركاتك
  •  

 

 

Flag Counter